消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

手报是否必须带插孔电话

物业交接查验时候发现除电梯前室外,其他手报都没带插孔电话通话功能,这个是否符合规范

清风抚凡心 | 2024-09-30 08:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

LHH2737 2024-09-30 09:53 10 [回复]举报

GB 50116-2013第6.7.4.22 设有手动火灾报警按钮或消火栓按钮等处,宜设置电话插孔,并宜选择带有电话插孔的手动火灾报警按钮。

只有局部设置其实也不算违反吧

清风抚凡心   回复: LHH27372024-10-09 10:38

情况是,消防电梯前室带插孔的手报可通话,其他部位带插孔不能通话,不知道是否符合规范

0    0 [回复]举报

安洪全 2024-09-30 11:19 00 [回复]举报

个人认为,物业交接的话,先看图纸,现场符合图纸,即认定为符合规范设计。


然后再看双方怎么约定的,是现状交房?还是验收合格后交房。


这个手报的事,大概率就是谈其他条件的筹码。

您指着上家公司给您全换成带插孔的,对后期运营的意义也不大。

潘天坤 2024-09-30 16:29 00 [回复]举报

这个不符合规范和实际要求,宜字也应遵循,一般设计和现场会选用带电话插孔的手动火灾报警按钮

清风抚凡心   回复: 潘天坤2024-10-09 10:38

情况是消防电梯前室带插孔的手报可通话,其他部位带插孔不能通话,不知道是否符合规范

0    0 [回复]举报

潘天坤   回复: 清风抚凡心2024-10-09 14:42

其他场所没有规定有提到可“不带有电话插孔”

0    0 [回复]举报

一直在路上_WlpS   回复: 清风抚凡心2024-10-11 09:34

依照图纸验收,有图依图无图依规

0    0 [回复]举报

关闭

关闭

手机APP下载