疏散指示灯安装高度是否能够调整

疏散指示灯装在距地面1m以下,被办公位遮挡不易看到,是否能够抬高设置?有没有相关规定?谢谢!

葫芦小金刚 | 2024-09-10 13:27
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

LHH2737 2024-09-10 14:25 30 [回复]举报

可以改成吊装的

4.5.11 方向标志灯的安装应符合下列规定:

1 应保证标志灯的箭头指示方向与疏散指示方案一致。

2 安装在疏散走道、通道两侧的墙面或柱面上时,标志灯底边距地面的高度应小于1m。

3 安装在疏散走道、通道上方时:

1)室内高度不大于3.5m的场所,标志灯底边距地面的高度宜为2.2m~2.5m;

2)室内高度大于3.5m的场所,特大型、大型、中型标志灯底边距地面高度不宜小于3m,且不宜大于6m。

葫芦小金刚   回复: LHH27372024-09-10 14:33

谢谢

0    0 [回复]举报

红门铠甲   回复: LHH27372024-10-11 14:24

老师好!疏散指示灯安装在疏散通道的消火栓门上,这个符合要求吗?谢谢

0    0 [回复]举报

LHH2737   回复: 红门铠甲2024-10-11 14:35

不符合,GB 51309-2018第4.5.1 条:

灯具应固定安装在不燃性墙体或不燃性装修材料上,不应安装在门、窗或其他可移动的物体上。

0    0 [回复]举报