消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

备用照明能否多个房间接一个回路

配电室、消防控制室、消防水泵房等发生火灾时仍需工作、值守的区域应同时设置备用照明;这些房间的应急照明都需要单独设置一个回路,那么备用照明呢,比如说两个配电室能否共用一个备用照明回路

LHH2737 | 2024-07-09 16:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

潘天坤 2024-07-09 17:56 00 [回复]举报

从设计来说,一般会接入附近的的消防开关箱内,开关箱展开图的接线一般也如此

共用回路的话,一不符合设计要求(详见开关箱展开图),二是可能线路会拉的比较远,个人觉得不一定比按图施工轻松

关闭

关闭

手机APP下载