请问4层2600平米大学公寓需火灾自动报警系统吗?

请问4层2600平米大学公寓需火灾自动报警系统吗?

消防网友62321 | 2024-07-01 17:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

LHH2737 2024-07-02 09:52 00 [回复]举报

要,虽然规范只是说中小学宿舍需设火灾自动报警,但是我咨询过一些专家都表示大学宿舍也要

秘密1 2024-07-02 10:20 00 [回复]举报

根据防火通用规范GB55037-2022第8.3.2条规定,4层2600平方米的大学公寓未有强制性要求设计火灾自动报警系统