消控室布置

根据规范在值班人员经常工作的一面,设备面盘至墙的距离不应小于3m 。操作面需要1.5m的操作空间,那么1.5-3米之间这段空间内布置其他设备或者布置监控工作台是否允许?

九九 | 2022-06-01 20:16
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

0_EHdk 2022-06-03 11:08 00 [回复]举报

可以布置在一排

周家斌 2022-06-04 10:06 00 [回复]举报

消防小学生刘振 2022-06-07 15:49 00 [回复]举报

可以,只要满足面盘距墙不小于3米,同时有1.5米的操作空间即可,不过也要看验收人员的理解,如果非要在1.5米至3米的空间内布置监控工作台的话,建议监控工作台与设备面盘按照双列布置考虑,保持一个2米的工作间距,这样做相对稳妥。