消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

主机故障比例不超过多少合规

从百度里搜出来这个标准,但是在规范里一直没找到,请教各位大佬指点下


国家标准《建筑消防设施设计规范》(GB 50016-2014)规定:消防报警主机的允许故障率不得超过5‰,即每1000个主机中允许出现5个故障。这是保障消防报警系统稳定运行的基本要求。


根据《火灾自动报警系统设计规范》(GB50116-2013),消防自动报警系统主机在设计和安装时,要求故障点位不能超过千分之三。这意味着在消控主机中,故障点位的数量不能超过总点位数的千分之三。

zhangbo | 2024-07-16 07:54
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

消防资源网 2024-07-17 08:14 10 [回复]举报

不要盲目看百度

灭邪斩 2024-07-17 08:44 10 [回复]举报

以下观点仅供参考:

1、主机故障比例、故障率、故障点位等未在《建筑消防设施设计规范》(GB 50016-2014)[2018版]和《火灾自动报警系统设计规范》(GB50116-2013)等规范术语及说明中体现。

2、关于火灾报警系统产品的合格判定详见《火灾自动报警系统施工及验收标准 GB50166-2019》规范。

3、关于火灾报警控制器产品合格判定详见《火灾报警控制器 GB4717-2005 》规范。

4、百度所得宜甄别对待。

关闭

关闭

手机APP下载