消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

合用前室加压送风口

图纸设计合用前室加压送风口设置于合用前室顶部,暖通图平面图竖井风管接水平管(70度防火阀-风口),自动报警图纸设计需要联动加压送风口,联系设计,设计回答为普通风口。

1119 | 2024-07-02 14:39
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

潘天坤 2024-07-02 18:44 00 [回复]举报

请问一共有几层前室有机械加压送风口,一般服务大于三层的前室的系统,前室需要设置手动开启装置,前室加压送风口为常闭

同时当防火分区内火灾确认后,应能在15秒内联动开启防火分区内着火层及其相邻上下层前室及合用前室的常闭送风口,同时开启加压送风机

建筑防烟排烟系统技术标准 GB51251-2017第3.3.6条规定:
加压送风口的设置应符合下列规定:2 前室应每层设一个常闭式加压送风口,并应设手动开启装置

建筑防烟排烟系统技术标准 GB51251-2017第5.1.3条规定:

当防火分区内火灾确认后,应能在15s内联动开启常闭加压送风口和加压送风机。并应符合下列规定: 2 应开启该防火分区内着火层及其相邻上下层前室及合用前室的常闭送风口,同时开启加压送风机

1119   回复: 潘天坤2024-07-03 17:31

负二至十八层都设置有送风口,风口标高要求不低于2.4m,手动开启装置是否可以与70度防火阀一起水平安装。

0    0 [回复]举报

潘天坤   回复: 11192024-07-03 17:53

手动开启装置肯定是距地设置的呢,要能够方便操作

常见执行机构在上方,下方为开启装置

0    0 [回复]举报

1119   回复: 潘天坤2024-07-03 21:37

执行机构如果安装在风口下方就到不到标高,水平安装距离也不够,能否把70度防火阀改成一个执行机构

0    0 [回复]举报

潘天坤   回复: 11192024-07-04 13:52

此区域的70℃防火阀是必须设置的,不能用执行机构(排烟阀)代替70℃防火阀

如果一种产品可以兼备70℃防火阀和常闭功能,并且能够提供与现场设备一致的70℃防火阀型式检资料,可以认可,其他情况个人认为是存在问题的

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

0    0 [回复]举报

关闭

关闭

手机APP下载