厂区内的车间,只与厂区内部道路相邻,长度超过150米,是否也应设置穿过建筑物的消防车道,确有困难时,应设置环形消防车道?

《建筑设计防火规范》GB50016-2014 (2018年版)第7.1.1条规定:当建筑物沿街道部分的长度大于150m或总长度大于220m时,应设置穿过建筑物的消防车道。确有困难时,应设置环形消防车道。请问:对于建在厂区内的戊类车间,该车间为非沿街建筑,该车间四周都不与城镇道路或街区道路相邻,只与厂区内部道路相邻,长度超过150米,是否也要执行7.1.1.条规定,即应设置穿过建筑物的消防车道。确有困难时,应设置环形消防车道?

qdczx | 2024-05-17 09:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防检查 2024-05-17 14:09 00 [回复]举报

个人观点,没必要。建规7.1.1和7.1.2针对的是民用建筑。7.1.3 工厂、仓库区内应设置消防车道。
    高层厂房,占地面积大于3000m²的甲、乙、丙类厂房和占地面积大于1500m²的乙、丙类仓库,应设置环形消防车道,确有困难时,应沿建筑物的两个长边设置消防车道。

消防君 2024-05-18 09:47 00 [回复]举报

消防车道的要求,不要单纯的看建规了,建议参考建筑防火通用规范,这里面规定的彩石需要强制落实的要求:

3.4.1 工业与民用建筑周围、工厂厂区内、仓库库区内、城市轨道交通的车辆基地内、其他地下工程的地面出入口附近,均应设置可通行消防车并与外部公路或街道连通的道路。

3.4.2 下列建筑应至少沿建筑的两条长边设置消防车道:    

1 高层厂房,占地面积大于3000m²的单、多层甲、乙、丙类厂房;    

2 占地面积大于1500m²的乙、丙类仓库;    

3 飞机库。

3.4.3 除受环境地理条件限制只能设置1条消防车道的公共建筑外,其他高层公共建筑和占地面积大于3000m²的其他单、多层公共建筑应至少沿建筑的两条长边设置消防车道。住宅建筑应至少沿建筑的一条长边设置消防车道。当建筑仅设置1条消防车道时,该消防车道应位于建筑的消防车登高操作场地一侧。

一路同行 2024-05-21 10:12 00 [回复]举报

戊类厂房没有必要