消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防排烟管道经过房间的时候,经过房间的排烟管需要做什么措施吗?(1、要防火包裹?2、穿越房间隔墙处要设置280°排烟防火阀?

da_n_d | 2021-03-03 10:40
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 9

小马 2021-03-03 11:19 00 [回复]举报

https://gf.1190119.com/article-27403.htm?keywords=0.5

4.4.7

http://gf.1190119.com/article-27524.htm

4.4.1

楼主可以参考一下,每个包房都看做一个防烟分区,支管接入房间,需设置一个280°c防火阀,

da_n_d   回复: 小马2021-03-03 16:55

好的,谢谢回答

0    0 [回复]举报

da_n_d   回复: 小马2021-03-03 16:58

我的风管只是经过房间,房间内没有设置排烟口,那是进出房间各设置一个280度排烟防火阀吗?

0    0 [回复]举报

小马   回复: da_n_d2021-03-04 09:20

楼下已经有老板给出了答案,只是经过房间不需要防火阀,

0    0 [回复]举报

大案 2021-03-03 13:50 00 [回复]举报

这个问题和你问的防火门的问题一样,每个包房都是独立的防火分隔单元,那设置280℃的防火阀就没有什么疑问了。

da_n_d   回复: 大案2021-03-03 16:56

我老板说风管要做防火包裹,但是我也没看到哪里写着要防火包裹。

0    0 [回复]举报

da_n_d   回复: 大案2021-03-03 17:02

我的排烟口用的是多叶电动排烟口(280度是自动关闭),所以图上的排烟口前没有设置280度排烟防火阀。我的风管只是经过房间,没有在房间做排烟,风管经过房间对风管有什么要求吗?

0    0 [回复]举报

刘丽波 2021-03-03 23:12 40 [回复]举报

排烟管道穿过本防火分区房间隔墙,不需要加设排烟防火阀。每个防烟分区支管需要设置排烟防火阀。具体见《烟规》4.4.10。所有排烟管道都要做满足耐火极限要求的防火包裹。

潘天坤 2024-07-01 13:51 00 [回复]举报

需要看穿越墙体是否为防火隔墙,是否为重要区域,常见就是对比此墙体是否有开设防火门,如果有防火门一般会认为是重要区域而设置排烟防火阀,当然这个不属于排烟防火阀的设防要求

如果需要设置排烟防火阀,那么穿越防火隔墙防火阀前后两米的防护保护措施也是少不了的

关闭

关闭

手机APP下载