储油罐区防火堤内的消防冷却水管道的四孔法兰是否需要做跨接?采哪个标准规范的条款?

储油罐区防火堤内的消防冷却水管道的四孔法兰是否需要做跨接?采哪个标准规范的条款?

目前查到GB50151《泡沫灭火系统设计规范》3.7.9对干式管道要做跨接。



那对冷却水管道的四孔法兰,是否跨接呢?

谢谢~

fenk11 | 2024-01-18 14:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

折耳根 2024-01-18 15:01 20 [回复]举报

3.7.9 对于设置在防爆区内的地上或管沟敷设的干式管道,应采取防静电接地措施,且法兰连接螺栓数量少于5个时应进行防静电跨接。钢制甲、乙、丙类液体储罐的防雷接地装置可兼作防静电接地装置。

阳明心 2024-01-19 08:52 00 [回复]举报

《工业金属管道工程施工规范》(GB 50235—2010)

第7.13.1条规定:设计有静电接地要求的管道,当每对法兰或其他接头间电阻值超过0.03欧时,应设导线跨接,可以看出,工业管道金属法兰是否跨接,需要测量法兰间电阻值。当法兰间电阻值超过0.03Ω时,应设导线跨接。


应该需要导线跨接