消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于气体灭火系统防护区容积

       设计对象为丙类二级厂房,用途数据中心。根据气体灭火设计规, 采用管网灭火系统时,一个防护区的面积不宜大于800m²,且容积不宜大于3600m³。本项目一个数据机房面积800平,但容积式4500左右,远超规范要求。但甲方以规范不是强条为由,要求使用气灭系统。想请教各位大佬,这种情况在设计时和工程实践中需要注意什么问题。

消防网友123 | 2023-09-22 10:47
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

张治福 2023-09-22 13:57 10 [回复]举报

加大灭火设计浓度值,或者增加气体灭火的瓶装数量。用容积进行折算

关闭

关闭

手机APP下载