消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水泵远程启泵线有没有规范要求一定用单芯线缆,用多芯电缆行不行?

消防水泵远程启泵线有没有规范要求一定用单芯线缆,用多芯电缆行不行?

消防小迷糊 | 2021-01-05 15:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

cgc 2021-01-06 21:34 00 [回复]举报

消防远程多线控制一般都是NKKVV电缆设计,第一因为属于消防线路,要满足耐火要求。第二,一台消防设备多线一般都是很多芯,单芯敷设相对多芯不利施工。一般在消防设备多线控制选型上很少有用单芯散开共走方式的。因此多芯控制电缆NHKVV是最好的选择。

关闭

关闭

手机APP下载