消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

餐饮店中的厨房防火门选用

餐饮店的厨房采用耐火极限不低于2.00h的防火隔墙与其他区域分隔,墙上的门窗是采用甲级还是乙级?


WeiHL | 2020-12-24 10:49
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

黄辉 2020-12-24 10:57 00 [回复]举报

6.2.3 建筑内的下列部位应采用耐火极限不低于2.00h的防火隔墙与其他部位分隔,墙上的门、窗应采用乙级防火门、窗,确有困难时,可采用防火卷帘,但应符合本规范第6.5.3条的规定:

    5 除居住建筑中套内的厨房外,宿舍、公寓建筑中的公共厨房和其他建筑内的厨房

胡工 2021-01-12 15:21 00 [回复]举报

乙级防火窗即可

周家斌 2022-05-10 10:56 00 [回复]举报

《建筑设计防火规范》 GB50016-2014(2018年版)6.2.3 建筑内的下列部位应采用耐火极限不低于2.00h的防火隔墙与其他部位分隔,墙上的门、窗应采用乙级防火门、窗,确有困难时,可采用防火卷帘,但应符合本规范第6.5.3条的规定:     1 甲、乙类生产部位和建筑内使用丙类液体的部位;     2 厂房内有明火和高温的部位;     3 甲、乙、丙类厂房(仓库)内布置有不同火灾危险性类别的房间;   4 民用建筑内的附属库房,剧场后台的辅助用房; 5 除居住建筑中套内的厨房外,宿舍、公寓建筑中的公共厨房和其他建筑内的厨房;     6 附设在住宅建筑内的机动车库。内部的灶具明火加工区域设置防火门分隔,其他不需要再进行划分。《饮食建筑设计标准 》JGJ64-20174.3.10 厨房有明火的加工区应采用耐火极限不低于2.00h的防火隔墙与其他部位分隔,隔墙上的门、窗应采用乙级防火门、窗。

关闭

关闭

手机APP下载