消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水池取水口

室外地下独立消防水池,在水池上方做个检修口,能不能作为水池取水口。

DZ王 | 2023-07-07 13:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

同同不同 2023-07-07 13:45 00 [回复]举报

不能

安洪全 2023-07-07 13:49 00 [回复]举报

检修口可以和取水口合用,但合用的检修口也要满足消防水池取水口的相关要求。


消防给水及消火栓系统技术规范 GB50974-2014

4.3.7 储存室外消防用水的消防水池或供消防车取水的消防水池,应符合下列规定:    

1 消防水池应设置取水口(井),且吸水高度不应大于6.0m;    

2 取水口(井)与建筑物(水泵房除外)的距离不宜小于15m;    

3 取水口(井)与甲、乙、丙类液体储罐等构筑物的距离不宜小于40m;    

4 取水口(井)与液化石油气储罐的距离不宜小于60m,当采取防止辐射热保护措施时,可为40m。


如果达不到相关要求的话,还是建议分开设置。

周家斌 2023-07-07 14:04 00 [回复]举报

满足取水口条件下可以直接从水池取水。

关闭

关闭

手机APP下载