消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

悬挂式灭火器能否替代七氛丙烷,符不符合规定?

您好,我这边有个疑惑,能向您这边咨询下不?我们公司设备房的气体灭火器(七氛丙烷)过期了,考虑成本问题,想用悬挂式干粉灭火器替代七氛丙烷,这样符合规定么?适用么

诗胜 | 2023-04-13 10:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

陈曲 2023-04-13 11:55 00 [回复]举报

按通用规范强条是等效替代,个人理解很多场景超细干粉是可以替代的

消防老胡 2023-04-13 12:22 10 [回复]举报

只要使用的电气设备没有特殊规定(因为干粉灭火剂灭火后,干粉发生反应附着在设备表面甚至深入内部电路板,很难去除,会导致设备损害甚至报废,造成经济损失,得不偿失),干粉灭火系统可以考虑替换七氟丙烷气体灭火系统。但有几个专业问题需要进行厂家或设计院进行深化设计:1是按分区应用还是局部应用系统?2是选用主动型还是被动型灭火系统?3是灭火剂设计用量的计算是否合理?4是布置高度,水平位置等因素是否科学?

南明离火 2023-04-13 14:08 00 [回复]举报

只要你不担心 灭火后因为干粉设备损坏  没问题

黄辉 2023-04-25 14:00 00 [回复]举报

首先判断柜式七氟丙烷灭火装置是否过期,不要被一些维保公司忽悠了。


焊接钢瓶使用年限是20年,无缝钢瓶的使用的年限一般是30年(《气瓶安全技术规程》TSG 23-2021实施后删除的是20年),具体可以看钢瓶上的钢印。


七氟丙烷药剂是没有过期的说法。


设备定期维护就可以。


然后再考虑设备房是否适合做悬挂式干粉灭火装置。如果符合干粉干粉灭火装置的相关规定,也是可以替换的。


更换还需要满足相关的法规要求,比如要做设计变更之类的。