正在使用单连锁改双连锁系统怎么弄

一高34米单层仓库,多层货架自喷系统正在使用单连锁预作用系统不充气体,为了防止误充水改双连锁系统要怎么施工安全可靠谢谢?

张恭 | 2023-04-11 16:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

简@风格 2023-04-11 18:22 00 [回复]举报

按双联锁的设计要求:增加空压机  更换报警阀组   参考这篇文章   说的很清楚  自喷预作用系统中单联锁和双联锁控制 https://www.idpi.cn/zichabaogao/1001687.html


希望能帮到你