关于防排烟系统中百叶风口的应用?

什么情况下可以使用普通的百叶风口作为排烟口?如果排烟支管使用百叶风口可以配一个常闭的280℃排烟防火阀吗?有常闭的280℃防火阀吗?

请大神赐教!!!感谢!!

清浅 | 2022-10-25 01:05
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

永锅 2022-10-25 09:18 00 [回复]举报

一个排烟风机负担一个防烟分区的排烟时,可使用常开的排烟口。

一个排烟风机负担多个防烟分区的排烟时,各防烟分区支管上设置常开的排烟防火阀和常闭的防烟阀。

清浅   回复: 永锅2022-10-28 20:11

有规范条文?哪个规范呀

0    0 [回复]举报

潘天坤 2024-07-01 15:43 00 [回复]举报

一台排烟风机只负责一个防烟分区的时候,一般就可以不设置常闭排烟口(电动充电桩这类的另当别论)

不知道市面上是否有常闭的排烟防火阀,如果有此类产品,能够实现功能,并且排烟防火阀具备防火性能(现场材料与报告一致),应该没问题