柴油发电机房内的储油间电气设备及管路(包括强电、弱电)必须是防爆的吗?有没有相应的规范支持?

请老师们给出相应规范要求

消防网友9071 | 2022-10-09 09:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

周家斌 2022-10-09 11:21 00 [回复]举报

无需防爆,

石油化工企业设计防火标准 GB50160-2008(2018年版)闪点小于60℃且大于或等于55℃的轻柴油,如果储罐操作温度小于或等于40℃时,其火灾危险性可视为丙A类,这点在老规范中是乙类的,现在有调整。

消防网友9071   回复: 周家斌2022-10-17 14:48

谢谢您的回复,建筑设计防火规范条文说明还有一句话(需要设置在建筑内的柴油设备或柴油储罐,柴油的闪点不应低于60°)。我想问一下丙类液体就不用设防爆电气了吗?柴油虽然挥发比较慢,但它是不是也有爆炸的可能,

0    0 [回复]举报