消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

高低压配电室的事故风机应该与消防系统联动吗?

高低压配电室均配置有七氟丙烷气体灭火系统,事故风机应该是气体灭火系统灭火后启动用于排七氟丙烷气体的,如果设置事故风机与消防系统联动,当该配电室两个火警信号触发时,事故风机可能还早于气体喷射,合理吗?

linkjim | 2022-08-10 13:36
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

周家斌 2022-08-10 13:56 00 [回复]举报

联动关闭防护区域的送(排)风机及送(排)风阀门、补风口的70°电动防火阀; 停止通风和空气调节系统及关闭设置在该防护区域的电动防火阀;事故风机的启动用室外手动启动装置启动。

消防网友62117 2022-08-12 17:30 00 [回复]举报

气体灭火喷洒前,气灭主机联动关闭灾后排风风口、风阀,如果是设置常闭风阀(口),仅在灾后排风时开启,就不用联动了,灾后风机通过手动装置开启

一个碳基生物 2022-08-29 19:36 00 [回复]举报

事故风机可以与消防联动,但仅限于火灾时关闭风阀,而不应联动启风机。

人为确定火灾扑灭后,通过控制柜或就地启停按钮启动风机。

创生Dauntless 2023-03-08 11:20 00 [回复]举报

火规第4.4.2条第3款,要求停止,而不是要求联动启动

关闭

关闭

手机APP下载