消防管道阀门到底采用软密封阀门还是硬密封阀门

一住宅项目消防图纸设计说明中:截止阀采用J41T;闸阀采用Z41H;蝶阀采用A型对夹式双向流;止回阀采用H44T;信号阀采用D371X。想知道在消防给水阀门中,正常使用的都是软密封阀门,本项目是否要按照设计说明必须采用硬密封阀门呢?求大师指点



| 2022-06-21 17:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

周家斌 2022-06-21 20:27 00 [回复]举报

按照设计要求做,硬密封的阀体耐用,软密封的优点是密封性能好,缺点是容易老化、磨损、使用寿命短。硬密封使用寿命长,但是密封性相对比软密封差。在消防水系统中,硬密封的密封性能够用了。

灵魂的动力 2022-06-22 11:40 00 [回复]举报

用软密封就行,没必要用硬密封。

周家斌   回复: 灵魂的动力2022-06-22 16:30

虽然都能用,不过还是以图纸设计为准,否则有的验收判定为未按照设计要求选用阀门,有的造价清单特征也有特定描述。