消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

喷淋的压力

报警阀室喷淋上腔的压力表和下腔的压力表比喷淋末端压力小是什么原因。

消防111111111 | 2021-10-25 15:52
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

乐清迦累得 2021-10-27 19:19 00 [回复]举报

如果报警阀位于末端的下部,压力表的显示还是显示压力读数小:①压力表选型错误, ②管路堵塞 ③有气囊 ④分区供水,不一定是一个系统, ⑤压力表的连接管径或相关阀门故障 ⑥压力表的规格错误,故障 ⑦其他原因

消防111111111   回复: 乐清迦累得2021-10-28 15:49

报警阀室上腔压力是系统侧压力表,下腔压力是供水侧压力表,我检查到的是供水压力小于系统侧压力,然后末端压力大于系统侧压力和供水侧压力 是否正常?

0    0 [回复]举报

阳明心 2023-04-14 15:06 00 [回复]举报

1、末端压力与报警阀系统侧压力对比取决于两者在高程上的相对位置;

2、供水侧压力小于系统侧压力可能是供水侧有漏,可能止回阀坏了。

关闭

关闭

手机APP下载