自动喷淋系统的设计流量怎么算?

请问各老师,自动喷淋系统的设计流量是如何计算的呢?规范上的计算方式确实有些看不懂。

学生 | 2021-08-03 11:49
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

pa119 2021-08-03 16:22 00 [回复]举报

要把作用面积内的所有喷头的流量求和。

最末端流量最小,根据公式q=k√10p最末端动压和喷头流量系数先算出最末端流量,然后计算出流速,再计算上一喷淋点位到末端端头的水头损失,计算出上一点位的动压,再根据q=k√10p计算出这个喷淋点位的流量。

以此类推算出作用面积所有喷淋点位的流量。

学生   回复: 一二一2021-08-05 09:31

我一个朋友说用喷水强度*作用面积/60就等于喷淋系统需要流量,设计流量在*1.3倍。

0    0 [回复]举报

学生   回复: pa1192021-08-05 09:38

虽然没看懂,但是假设一般末端压力p取最小值0.05,采用标准喷头k取80,那么这个公式求出来的值就是一个固定值啊?

0    0 [回复]举报

一棵松   回复: 学生2021-09-07 08:57

这样粗略的估计是没有问题的,按照细算,得先算一个喷头的保护面积,按照最不利最小保护面积计算出多少个喷头同时开启,在合计此面积内喷头的总流量。

0    0 [回复]举报