商场同个楼层同一个防火分区的的商店与公共通道相互接壤的玻璃隔墙,是否需要满足2小时耐火隔热需求?

通道为公共走道,围绕中庭环形,商铺位于走道外侧,走道内侧为中庭,上铺与走道接壤的玻璃隔墙是否需要满足 2小时耐火隔热需求?

北小望 | 2025-06-16 16:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

小唐12321 2025-06-16 17:05 00 [回复]举报

建筑内设置中庭时,其防火分区的建筑面积应按上、下层相连通的建筑面积叠加计算;当叠加计算后的建筑面积大于本规范第5.3.1条的规定时,应符合下列规定:     1 与周围连通空间应进行防火分隔:采用防火隔墙时,其耐火极限不应低于1.00h;采用防火玻璃墙时,其耐火隔热性和耐火完整性不应低于1.00h,采用耐火完整性不低于1.00h的非隔热性防火玻璃墙时,应设置自动喷水灭火系统进行保护;采用防火卷帘时,其耐火极限不应低于3.00h,并应符合本规范第6.5.3条的规定;与中庭相连通的门、窗,应采用火灾时能自行关闭的甲级防火门、窗;     2 高层建筑内的中庭回廊应设置自动喷水灭火系统和火灾自动报警系统;     3 中庭应设置排烟设施;     4 中庭内不应布置可燃物。

罗马苏丹 2025-06-16 17:26 00 [回复]举报

满足1小时即可,可以看看建筑设计防火规范的5.3.2和5.3.6,虽然5.3.2被废止了,还是有参考意义的

牛丫头消防课堂 2025-06-16 18:30 00 [回复]举报

先看中庭与回廊之间是否了进行分隔,如果进行了分隔,那么你说的玻璃至少满足疏散走道墙体的耐火极限。

李勤 2025-06-17 08:26 00 [回复]举报


本身疏散通道要求1H耐火极限。