消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

低压压力开关和电接点压力表的区别

水泵房用的低压压力开关可以换成电接点压力表吗?

消防打工人 | 2025-03-13 10:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

小唐12321 2025-03-13 11:09 00 [回复]举报

不设置停泵信号应该功能差不多。

EHS专家-DL 2025-03-13 14:50 20 [回复]举报

根据《消防给水及消火栓系统技术规范》(GB50974-2014),电接点压力表可作为消防水泵出水干管低压压力开关的替代方案‌。其通过设定压力下限触发启动信号,实现联动控制消防泵的功能。电接点压力表需仅使用‌下限触点信号‌作为启泵触发,避免因误设上限值导致消防泵自动停泵(违反规范强制要求)‌,可以通过接线方式来合规。

但是也是注意到水泵房消防泵出口压力开关属于专用低压压力开关,其灵敏度与可靠性高于普通电接点压力表,直接替代可能降低系统稳定性‌;同时若电接点压力表选型不当(如触点容量不足)或维护缺失,可能导致触点粘连、氧化等问题,影响消防泵正常启动‌,所以替换后的电接点压力开关定期维护校验‌显得比较重要。

关闭

关闭

手机APP下载