仓库喷淋管网中,格栅式喷淋给水管网如何计算?

仓库喷淋喷头采用早期抑制快速咱应喷头(ESFR)时,经常会采用格栅式喷淋给水系统来减少管径及系统流量,那么这种给水系统如何计算?

我要吃饺子 | 2025-01-13 11:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

EHS专家-DL 2025-03-11 15:24 00 [回复]举报

一、设计参数选取 ‌

1.喷头性能指标‌:ESFR喷头流量系数‌K≥161‌(常见型号K=202),响应时间指数‌RTI≤28±8(m·s)⁰.⁵‌,额定工作压力‌1.2MPa‌,最大适用净空高度‌≤12m‌‌。 喷头布置间距需满足标准覆盖面积要求,通常不超过3.7m×3.7m‌。‌

2.系统类型限制‌:ESFR喷头仅适用于‌湿式系统‌,不得用于干式或预作用系统‌。


二、水力计算方法 ‌

1.作用面积与喷头数量‌:格栅式系统的作用面积应覆盖整个保护区域,单个喷头保护面积按规范确定‌。需计算‌同时作用喷头数量‌,通常取作用面积内所有喷头同时动作‌。‌

2.管道水力计算‌ ‌管径选择‌:通过‌流量-管径关系公式‌(如海曾-威廉公式)计算管道摩擦损失,结合喷头工作压力(≥0.35MPa)确定最小管径‌。‌节点压力平衡‌:逐段计算管道沿程和局部水头损失,确保各喷头实际工作压力与流量满足设计要求‌。‌

3.系统总流量与压力‌ ‌总流量‌:按作用面积内所有喷头流量叠加计算,且不低于规范要求的最小设计流量(如140L/s)‌。‌泵组扬程‌:需满足最不利点喷头工作压力要求,并考虑高程差及管道总水头损失‌。