消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请各位老师看一下这个一次消防用水的问题

一个室外预制舱电化学储能站,只有电池舱有水系统,设计流量为10.8l/s,室外消火栓20l/s,设计灭火冷却降温1小时,一次消防用水量设计为254.88m³,这是咋算的,咋算都算不到,没有室内消火栓那些。

消防小萌新 | 2024-12-04 08:48
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

jinyanwu 2024-12-04 09:29 10 [回复]举报

个人意见,仅供参考:

从你提供的数据,这个储能站的室内消防是按照一个小时的火灾延续时间,室外栓是按照3个小时的火灾延续时间计算的,则能够算出来消防用水量为(10.8+20*3)*3600/1000=254.88m³。

消防小萌新   回复: jinyanwu2024-12-04 12:43

非常感谢您,刚看了预评价报告,是这样设计的

0    0 [回复]举报

关闭

关闭

手机APP下载