七氟丙烷气体灭火系统喷嘴处的气体流速范围大约是多少?

喷嘴面积都很小,是多大的流速才能充满全室,应该没有超音速吧?

zzyzy | 2024-06-02 21:06
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

香.香 2024-06-03 13:22 00 [回复]举报

气体灭火系统保护的防护区所需要的灭火剂的储存量是需要根据防护区的面积或体积来进行计算的。灭火剂的喷洒时间也是有要求的,它根据灭火剂的不同种类以及其所保护的场所的使用性质来要求的。比如七氟丙烷灭火剂当用于保护计算机房时,要求其喷放时间不大于8秒,而当它保护其它场所时,时间不大于10秒。在设计的时候只需要满足要求就可以了,足量的灭火剂,规定时间,合规的喷头间距以及喷头的喷射率等。