电梯开向走道,是否需要防火卷帘进行分隔?

如图所示,电梯未做电梯前室,直达走道,是否需要增设防火卷帘将电梯进行分隔?

澜沐 | 2023-09-19 15:18
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

张治福 2023-09-19 15:30 00 [回复]举报

首先,防火卷帘是不能使用的。

第二,如果是客梯,不需要进行防火分隔。

第三,如果是消防电梯,需要按道消防电梯前室的要求进行防火分隔。

yizhongdayang 2023-09-20 16:50 00 [回复]举报

《建筑设计防火规范》(GB50016-2014,2018年版)5.5.14 公共建筑内的客、货电梯宜设置电梯候梯厅,不宜直接设置在营业厅、展览厅、多功能厅等场所内。老年人照料设施内的非消防电梯应采取防烟措施,当火灾情况下需用于辅助人员疏散时,该电梯及其设置应符合本规范有关消防电梯及其设置要求。

《建筑设计防火规范实施指南》5.5.14实施要点:公共建筑内的电梯 (客用电梯、无障碍电梯、货运电梯等),特别是直接开向商店营业厅、展览厅内的电梯,因不要求设置防烟前室,仅电梯层门有耐火要求,难以有效阻止烟气和火势自电梯竖井蔓延。因此,设计要考虑尽量在每个楼层设置电梯厅,并在电梯厅的入口处设置防火隔墙和甲级或乙级防火门,如不设置门,则应设置挡烟垂壁


我是小鱼鱼 2023-09-21 17:28 00 [回复]举报

客梯不需要。电梯门有耐火完整性要求。