消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

多层的甲类厂房,就一个防火分区,可以按整体计算泄爆吗,如果楼板换成钢格栅板,是不是就可以按 整体计算了

多层的甲类厂房,就一个防火分区,可以按整体计算泄爆吗,如果楼板换成钢格栅板,是不是就可以按 整体计算了

正在学习中 | 2023-05-23 09:08
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

陈曲 2023-05-23 12:32 00 [回复]举报

按整体没问题

如果是考试 建议就不要看这种问题了


安洪全 2023-05-23 14:47 00 [回复]举报

有爆炸危险的部位才需要泄压,整体都有?

多层的话不可能仅在一处泄压,之所以计算泄压面积前要考虑长径比的问题就是为了均匀设置。

建筑设计防火规范 GB50016-2014(2018年版)

3.6.3 泄压设施宜采用轻质屋面板、轻质墙体和易于泄压的门、窗等,应采用安全玻璃等在爆炸时不产生尖锐碎片的材料。    

泄压设施的设置应避开人员密集场所和主要交通道路,并宜靠近有爆炸危险的部位。    

作为泄压设施的轻质屋面板和墙体的质量不宜大于60kg/m²。    

屋顶上的泄压设施应采取防冰雪积聚措施。


3.6.4 厂房的泄压面积宜按下式计算,但当厂房的长径比大于3时,宜将建筑划分为长径比不大于3的多个计算段,各计算段中的公共截面不得作为泄压面积


3.6.7 有爆炸危险的甲、乙类生产部位,宜布置在单层厂房靠外墙的泄压设施或多层厂房顶层靠外墙的泄压设施附近。

安洪全 2023-05-23 16:23 00 [回复]举报

我又看了一遍您的问题,确实是开脑洞。

如果楼板换成钢格栅板,钢格栅板能满足楼板的防火分隔要求吗?

或者说前提就变了,不是多层甲厂,而是单层甲厂。如果是单层甲厂,也要考虑长径比的限制,大于3时,也是要分段设置的。

我是小鱼鱼 2023-06-13 13:37 00 [回复]举报

关于这个问题,我咨询过化工院专家,按专家的意见是如果是砼楼板需要分层计算,如果是镂空格栅板,可以整体计算。

正在学习中   回复: 我是小鱼鱼2023-06-25 17:37

谢谢,后来跟一些老师沟通的也是可以按整体计算的,因为爆炸冲击力可以通过格栅进行流通

0    0 [回复]举报

设计规范   回复: 正在学习中2024-02-29 08:15

是整体做格栅板么,还是说满足50%就可以了

0    0 [回复]举报

正在学习中   回复: 设计规范2024-03-16 17:04

我这个是整体设置的

0    0 [回复]举报

关闭

关闭

手机APP下载