消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消控室和设备房门窗要求

消控室直通室外的门可以不是防火门吗?如果采用非防火门与周边的窗户和洞口有距离限制没?可以设置非防火的窗户吗?与周边窗洞的间距有要求没

消防学前班 | 2022-08-08 16:04
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

周家斌 2022-08-08 16:45 00 [回复]举报

对外可以是普通门,只要相邻或相对没有防火间距、楼梯间及前室需要洞口两侧距离等要求。就可以普通门窗。

消防学前班   回复: 周家斌2022-08-09 08:58

有量化距离要求没

0    0 [回复]举报

周家斌   回复: 消防学前班2022-08-09 14:11

看部位了,具体情况不一样,防火墙体两侧实体墙2米,内角4米,楼梯间及前室需要洞口两侧距离1米,为了满足防火间距设置防火门窗的等等!太多了!具体情况具体要求。

0    0 [回复]举报

消防学前班   回复: 周家斌2022-08-09 15:44

主要是消控室只是防火隔墙,找不到依据

0    0 [回复]举报

关闭

关闭

手机APP下载