消防救援口是否需要遵循不小于20米的规定

建规条文7.2.5 有要求,救援串口间距不宜大于20m且每个防火分区不应少于2个,而22年的通用规范里已经没有提到这个了,是否还需要遵循这个不大于20米的要求?


增某某 | 2025-03-08 14:38
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


精彩评论

EHS专家-DL 2025-03-11 12:15

‌1、技术要求保留性‌:若新规范未明确废止原条款,且原条款与通用规范无冲突,则原技术要求仍应执行‌。目前消防审查实践中,仍普遍沿用“20m间距”要求,因其直接关联消防救援效率‌。‌

2、规范衔接原则‌ 根据《建筑防火通用规范》实施指南,未细化规定的技术要求,应参考原规范或相关专业标准执行‌。消防救援口间距20m的限值属于技术细节,需通过配套文件(如地方消防技术指南)补充明确‌。


建议按照保守执行原则来做。若局部区域无法满足20m间距,需通过消防性能化设计或专家论证,证明替代方案等效安全‌。

查看原文
回答 | 4

我头发贼黑 2025-03-08 15:09 00 [回复]举报

遵循

尹先生 2025-03-08 23:28 00 [回复]举报

通用规范是把分散在各个规范里的强制条文做了汇总,原来的规范里的非强制条文转为推荐性标准,你可以看通用规范的前言,看这条是否被废止。

小唐12321 2025-03-10 09:41 00 [回复]举报

要的,如果都按照通规,那很多都是各人干各人的了。

EHS专家-DL 2025-03-11 12:15 00 [回复]举报

‌1、技术要求保留性‌:若新规范未明确废止原条款,且原条款与通用规范无冲突,则原技术要求仍应执行‌。目前消防审查实践中,仍普遍沿用“20m间距”要求,因其直接关联消防救援效率‌。‌

2、规范衔接原则‌ 根据《建筑防火通用规范》实施指南,未细化规定的技术要求,应参考原规范或相关专业标准执行‌。消防救援口间距20m的限值属于技术细节,需通过配套文件(如地方消防技术指南)补充明确‌。


建议按照保守执行原则来做。若局部区域无法满足20m间距,需通过消防性能化设计或专家论证,证明替代方案等效安全‌。